Maybe I didn't explain myself very well. The grounded corner delta is a way to have a 3 wire system and trip the OCPD rather than energize building parts. This is how it prevents the capacitive buildup of high voltages when a part of an armiture goes to ground on an electric motor. As the armiture spins around it makes contact with the metal frame. This causes high voltages to devleop.
Here is a ~50-year-old account of the perils on LV ungrounded systems?as opposed to high-resistance grounded systems. This all-time classic description is detailed in a chapter on system grounding in Beeman?s "Industrial Power Systems Handbook". [
"Chapter 6 --- System Grounding
About midafternoon one day in a West Coast manufacturing plant, normal operations became suddenly disrupted. The first evidence of trouble came in the form of a motor failure on the 480-volt system, then another, and still another in close succession. An inspection of switchboard
voltmeters (measuring line-to-line volts) and ammeters indicated no unusual conditions. System equipment continued to fail. A test voltmeter
was rigged up having a full-scale calibration of 1200 volts. Upon connecting it phase-to-ground, the pointer went off scale. A phase-to-ground potential on a 480-volt system of more than 1200 volts
existed!
At once the incoming service transformers were suspected of internal breakdown between high- and low-voltage windings. As the last of these
transformers was isolated and individually tested, it became evident that they were not at fault. System equipment continued to fail, and the
situation was desperate.
A frantic group went into a huddle and decided that the only way out was to trip the main incoming service breaker which would deenergize the
entire system. At this point one of the workmen noticed a small wisp of smoke coming from a motor-starting autotransformer and, upon
approaching, could hear a buzzing noise inside. This circuit was switched clear of the system, and the overvoltages disappeared. During the two-hour period that this arcing fault existed, between 40 and 50 motor windings had failed.
Finally it was found that the autotransformer enclosing case had been hashed in and was practically in contact with the coil. The spot where arcing had taken place was evident although not badly burned. An attempt was made to show the plant engineer what had been the trouble. A solid
connection was made between the frame and the burned spot on the coil. Much to the bewilderment of the operating men and according to the
expectations of the plant engineer, no more than the 73 per cent increase in the voltage to ground on the other two phases occurred. The main ingredient of the overvoltage (discontinuous conduction) had been omitted.
This is an actual case of severe prolonged experience of overvoltage of repetitive restrike origin on a 480-volt ungrounded system. This story
is spectacular because of the magnitude of the disturbance and consequential damage. Similar occurrences of lesser extent are not
uncommon, however, and there is evidence that they are more frequent than realized. It is a characteristic of ungrounded systems that they
are subject to relatively severe transient overvoltages. This trouble can be avoided by proper grounding of the system, and other important
benefits are also obtained."
pp. 337-338 L. J. Carpenter and L G. Levoy, Jr.
"Industrial Power Systems Handbook"
DONALD BEEMAN, Editor
Manager, Industrial Power Engineering / Industrial Engineering Section,
General Electric
McGRAW-HILL BOOK COMPANY, INC. 1955