Re: transformers
I had a unique opportunity to have an assignment as an application engineer for molded case circuit breakers (MCCB)and dry type distribution transformers (DTDT) I was given challenge by the DTDT product line manager to study the relationship between MCCBs and DTDTs because of warranty claims due to nuisance tripping. With my breaker background I partnered with a DTDT design engineer who gave be some 'ballpark' inrush values for various DTDT KVAs and designs. Since there has been no reason to actually test each transformer to get accurate values the actual values were not available. My study was not intended to be a "silver bullet" to solve problems but to help determine where there could be a problem with a Pri. OCPD/DTDT combination that may cause nuisance trips of the pri. OCPD.
75kva, 480v-208y/120 transformers are notorious for having the primary OCPD being undersized. One of the reasons in the panelboard that feeds the transformer may be limited to 100a frame breakers. The consultant or contractor concludes it's not going to be that loaded anyway and 100a max is just fine. But, the transformer inrush is overlooked.
The inrush to energize a 150deg 75kva transformer is about 10x the FLA, or 90 x 10= 900a. The inrush is even greater when you go to 115 and 80degC, K4 and K13 transformers. Because of lower losses and less winding resistance that inrush may increase to as much a 60% of the FLA or about 1400a. A 90a breaker's magnetic calibration is normally 10x it?s rating or 900a with a +-20% tolerance. So with a 150degC transformer it places you in a marginal situation to begin with. Yes, you are allowed to go 125% or 113a, which can be rounded to a 125A-rated breaker. Even a 125a MCCB may get a bit marginal when you apply an 80degC or K13 transformer, again 125a x 10=125a (+-20%) and you may be looking at 1400a of inrush.
Again, this is a ball park study to help determine where you could have a design problem and to be cautious or to help determine if there may be an inrush/OCPD conflict which is causing nuisance tripping. If you're going to cut things close it is important to know the risks so there won't be any suprised. I personally would prefer knowing what trouble I may be getting into before hand instead of being surprised and having to get out of deep dew-dew after the fact which can be $$$ and getting people just plain ornery and irritated.