Transformers
Redsilverado88
New member
Boston
There is a dry Siemens transformer on the job I'm on. There is fiberglass installation (the type you put in walls) on the inside. Can anyone tell me if this ok and allowed? I'm wondering if I can get an extra to change this transformer.
Now that your inquiry has sat here 5 hrs without a reply I'll start the ball rolling for you.
If I understand you correctly there is a Siemens "ventilated" dry type distribution transformer that someone has applied some fiberglass insulation 9ver the outside of the enclosure. If so some concluded that it would help to reduce the sound level.
Again, your inquiry is such as it causes a lot of reading between the lines. If someone added blanket insulation to the outside to reduce the sound level then the transformer is probably located in a office or other quiet area where and transformer noise would be noticeable. Like the term hot or cold noise is a relative term, noise bing measured in db@3m.
I would like to understand that the person who added the insulation did not cover or abstruct the ventilation openings,.
Now, if my assumptions are correct what would you need to know?
Custom transformers can be made with reduced sound levels but they still make some noise. In an area that is expected to be quiet any noise can be viewed as being loud.
Some GE transformers come with insulation on the inside as well.
Your best bet is to call Siemens or just try to look up the instruction manual on online using the catalog number.