250.30(A)(4) Grounding Electrode. The grounding electrode shall be as near as practicable to and preferably in the same area as the grounding electrode conductor connection to the system. The grounding electrode shall be the nearest one of the following:
(1)An effectively grounded structural metal member of the structure
(2)An effectively grounded metal water pipe within 1.5 m (5 ft) from the point of entrance into the building
Exception: In industrial and commercial buildings where conditions of maintenance and supervision ensure that only qualified persons service the installation and the entire length of the interior metal water pipe that is being used for the grounding electrode is exposed, the connection shall be permitted at any point on the water pipe system.
(3)Other electrodes as specified by 250.52 where the electrodes specified by 250.30(A)(4)(1) or (A)(4)(2) are not available
Exception to (1), (2), and (3): Where a separately derived system originates in listed equipment suitable for use as service equipment, the grounding electrode used for the service or feeder shall be permitted as the grounding electrode for the separately derived system, provided the grounding electrode conductor from the service or feeder to the grounding electrode is of sufficient size for the separately derived system. Where the equipment ground bus internal to the service equipment is not smaller than the required grounding electrode conductor, the grounding electrode connection for the separately derived system shall be permitted to be made to the bus.