Just got drawings 200 amp 480v 3 phase service for a 4- 8000 sq foot wharehouse complex.Minimal load for each space at this time.About a 11kw load.All gas heating and water heaters. No kitchens at this point.The engineer is calling for 15 kva transformers to feed each warehouse.Then calling for a 200 amp main lug panel( 120 /208) in each space. The transformers will be right next to the 200 amp panels .My question if properly protected on the primary side is this a violation?They have#12's on 25 amp breakers for the primary protection??? what is the smallest wire i can use on the load side?They have # 10"s.Everthing seems to be way undersized.Also would you not need secondary protection?Some times i miss somthing when it commes to transformer sizing