Transformers

Status
Not open for further replies.

Harry Rush

New User
Location
Buffalo
Occupation
Electrical
Is it permitted to have two separate load factors on one transformer? Can you come off the secondary side of a transformer to a disconnect with 3/0 and come out the same transformer secondary to a panel with a main breaker with 1/0?
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Yes. You can feed up to six panels/disconnects from the transformer secondary as long as you provide overcurrent protection as prescribed.
(See Note 2 to 450.3(B))
 