T TOM1187 Member Location United States Occupation Electrician Mar 15, 2022 #1 I have a 75KVA Transformer and I need to get 200 A on the secondary,side what is the calculation I need to do to get my primary breaker size?
I have a 75KVA Transformer and I need to get 200 A on the secondary,side what is the calculation I need to do to get my primary breaker size?
ptonsparky Tom Location NE (9.06 miles @5.9 Degrees from Winged Horses) Occupation EC - retired Mar 15, 2022 #2 TOM1187 said: I have a 75KVA Transformer and I need to get 200 A on the secondary,side what is the calculation I need to do to get my primary breaker size? Click to expand... You should include voltage somewhere.
TOM1187 said: I have a 75KVA Transformer and I need to get 200 A on the secondary,side what is the calculation I need to do to get my primary breaker size? Click to expand... You should include voltage somewhere.
T TOM1187 Member Location United States Occupation Electrician Mar 15, 2022 #3 ptonsparky said: You should include voltage somewhere. Click to expand... 480 primary 120/208 Secondary
ptonsparky said: You should include voltage somewhere. Click to expand... 480 primary 120/208 Secondary
electrofelon Senior Member Location Cherry Valley NY, Seattle, WA Occupation Electrician Mar 15, 2022 #4 Check out table 450.3(B).