charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Retired Electrical Engineer
What are the symptoms? Just saying it doesn't work is not enough information for us to help you.
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
NissanTitan08 said:
I have a 480v 3p primary delta primary, 120/240 secondary Y transformer. Why am I only getting one leg working in the panel.

No you don't.
You have either a delta-wye of 480-208Y/120 3PH 4w, a delta-wye of 480-240Y/136 3PH 4W, or a delta-delta of 480-240/120 3PH 4W.

What 10 voltages are you getting?

Vab
Vbc
Vca
Van
Vbn
Vcn
Vag
Vbg
Vcg
Vng
 