What Is O.c.p. On The Primary Side Of A 45 Kva Transformer. The Voltage Is 480/277
Bob, Table 450.3 does'nt allow rounding up over 250%. 135 amps would be the maximum if they made that size, otherwise i see it at 125 amps.iwire said:Any OCPD between 1 and 150 amps could be legal.
RUWired said:Bob, Table 450.3 does'nt allow rounding up over 250%.