Transformer KVA is determined by the connected load. So do a load calculation.
If you are keeping the same loads, and the present transformer is not overloaded, then a transformer with the same KVA rating should be sufficient.
If you want to switch to a wye connected secondary simply for grounding reasons, and not to add any neutral load, then you might consider using some sort of grounding transformer, eg. a 'zig-zag' transformer, which you _add_ to your current setup to derive a neutral for grounding purposes.
6.6 KVA seems a strange number for a transformer rating.
-Jon