Transformers

Status
Not open for further replies.

David Jimenez

New member
If you have a transformer, 15 KVA or greater, 50ft or more away form the electrical room do you need to have a means of disconect with in site of the transformer?
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
If you have a transformer, 15 KVA or greater, 50ft or more away form the electrical room do you need to have a means of disconect with in site of the transformer?
No transformer requires a "local" disconnect.

While they do require primary overcurrent protection, there is no requirement as to its placement.
 