lmichael310
Member
- Location
- Los Angeles, CA
Hi I am a new user here and I am trying to increase my design experience. I am working on a design to light a walkway. There are 19 luminaires to be installed in series along a walkway staggered by 100 ft and the luminare rating is 150 W. I have a 480 V 1P 3W from a substation and I want to see if my design approach is correct. First I found the VA for each luminare to be 265 voltamps, giving me a current of .55A at the last luminare and a current of 10.49 at the first luminare. The total load I caluclated as 10.49*1.25=13.11. Which gave my a 15 amps for the OCD at the panel. I then sized the wire to have a VD less than 3% and I get a #6 wire. One question I did have is how do i select the ground wire size, its based on OCD correct?
Thanks in advance for you help
Thanks in advance for you help