We often encounter flush mount combination service entrance device (CSED) panels like in the attached photo.
When adding additional equipment, I have never been able to find a code compliant way to transition from the flush panel to an exterior LB, gutter, or NEMA 3R box. Typically, we cannot access the back side of the panel (interior living space) and we often need to pull in more than just a feeder (if we did, NM cable would be fine).
When relocating 10 or 14 #12 and #14 branch circuits, for example, there’s simply no way to fit that much NM into the bottom or top of the flush mount panel.
What we usually do, is install an LB (like in the photo) with a chase nipple and bushing at the flush mount panel. We then run THWN for all circuits and wrap the 6-8” section of “free air” conductors running inside the wall from the LB to the top or bottom of the panel. We seal the penetration with an appropriate sealant.
I don’t like it, but there’s no fitting that can make that tight of a bend radius. Nor will flex conduit make it, LFMC, or anything else I’ve found.
That don’t make flush mount NEMA 3R boxes.
Does anyone have a better solution?
When adding additional equipment, I have never been able to find a code compliant way to transition from the flush panel to an exterior LB, gutter, or NEMA 3R box. Typically, we cannot access the back side of the panel (interior living space) and we often need to pull in more than just a feeder (if we did, NM cable would be fine).
When relocating 10 or 14 #12 and #14 branch circuits, for example, there’s simply no way to fit that much NM into the bottom or top of the flush mount panel.
What we usually do, is install an LB (like in the photo) with a chase nipple and bushing at the flush mount panel. We then run THWN for all circuits and wrap the 6-8” section of “free air” conductors running inside the wall from the LB to the top or bottom of the panel. We seal the penetration with an appropriate sealant.
I don’t like it, but there’s no fitting that can make that tight of a bend radius. Nor will flex conduit make it, LFMC, or anything else I’ve found.
That don’t make flush mount NEMA 3R boxes.
Does anyone have a better solution?