IMO technically you can't strip NM and run it in a raceway. Romex inner conductors are not an approved NEC conductor on their own.How much of the Romex do we have to strip to do this? 2 pieces of Romex would be over 31% of the 3/4" area, but 6 #12 are not over 40%.
View attachment 2563283
protective sleeves for cables have no fill requirements.To answer the question, you would strip the romex just after the clamp. I've done this many times in basements, never been failed for it. As mentioned, if under 24" you don't need to worry about fill.
In this case, the raceway is more than 24" long.protective sleeves for cables have no fill requirements.
For actual raceways there is no ampacity adjustment required for less than 24 inches, fill wise you still have a 60% limit for these short raceways.
Is this a basement or crawl space?In this case, the raceway is more than 24" long.
Sleeve should be between 18" and 10 ft.In this case, the raceway is more than 24" long.
Any particular reason why it should be within those dimensions?Sleeve should be between 18" and 10 ft.
Any particular reason why it should be within those dimensions?
That is true. I agree, I think it’s 310.120IMO technically you can't strip NM and run it in a raceway. Romex inner conductors are not an approved NEC conductor on their own.
In, as in through the hollow core, or surface mounted?It is in a CMU wall, the conduit runs up about 10 feet from an outlet box at 18" AFF through the top plate.
In the hollow core, where they should have just fished the NM cable to begin with.In, as in through the hollow core, or surface mounted?