I just got called out by an inspector for using type NM in a wet location.
The installation has a 40 amp NM feeder running through the attic, then penetrates the exterior wall and is run in PVC conduit down about 4 feet to a small surface mounted breaker panel. That breaker panel serves as a disconnect for a heat pump as well as feeds a dedicated service receptacle for said heat pump
My question is regarding the use of NM cable where it transitions from dry location to wet. Where is an approved location to transition from dry rated wiring (NM) to wet rated wiring (THWN, UF, etc.)? I could clearly transition inside the house in the attic. But what about a surface mounted exterior junction box right where it penetrates the wall? If that's NOT approved, then am I to assume that any wiring that penetrates a wall from dry to wet/damp location should be damp/wet rated, even if it's going straight into a light box or receptacle box etc.?
Furthermore, if I AM allowed to use dry rated wiring to feed a receptacle/light box, at what point is dry wiring not allowed? If I run through a 6" conduit to feed a light/receptacle? 12" conduit? 24" conduit?
Does anyone out there use damp/wet rated wiring when feeding exterior outlets or lights? Even if feeding into the back of a surface mounted box or recessed box?
In another forum (http://forums.mikeholt.com/showthread.php?t=168212) it is implied that a recessed junction box would likely be considered dry location whereas a surface mounted maybe not.
The installation has a 40 amp NM feeder running through the attic, then penetrates the exterior wall and is run in PVC conduit down about 4 feet to a small surface mounted breaker panel. That breaker panel serves as a disconnect for a heat pump as well as feeds a dedicated service receptacle for said heat pump
My question is regarding the use of NM cable where it transitions from dry location to wet. Where is an approved location to transition from dry rated wiring (NM) to wet rated wiring (THWN, UF, etc.)? I could clearly transition inside the house in the attic. But what about a surface mounted exterior junction box right where it penetrates the wall? If that's NOT approved, then am I to assume that any wiring that penetrates a wall from dry to wet/damp location should be damp/wet rated, even if it's going straight into a light box or receptacle box etc.?
Furthermore, if I AM allowed to use dry rated wiring to feed a receptacle/light box, at what point is dry wiring not allowed? If I run through a 6" conduit to feed a light/receptacle? 12" conduit? 24" conduit?
Does anyone out there use damp/wet rated wiring when feeding exterior outlets or lights? Even if feeding into the back of a surface mounted box or recessed box?
In another forum (http://forums.mikeholt.com/showthread.php?t=168212) it is implied that a recessed junction box would likely be considered dry location whereas a surface mounted maybe not.