jeremyinAZ
New User
- Location
- Phoenix
- Occupation
- Program Manager
Installing DC fast chargers throughout Colorado. Original contractor installed 3" Schedule 40 in hand-holes, preparing for the site to be "make-ready." Unfortunately, the 3" conduits are not in the right layout for the new charger. We proposed excavating the area down 24", then adjusting the 3" to the right layout. Very expensive to do- customer suggested we just install 3" LFMC onto the 3", then pour the footing around it, so we don't have to excavate.
I'm finding conflicting articles to support LFMC as an option.
350.6 says I CAN use LFMC encased in concrete. Assuming I can get a LFMC fitting that transitions from LFMC to Schedule 40- can that be buried in concrete?
Any help clarifying if I CAN encase the fitting in concrete- or article showing why I can't- would be greatly appreciated.
I'm finding conflicting articles to support LFMC as an option.
350.6 says I CAN use LFMC encased in concrete. Assuming I can get a LFMC fitting that transitions from LFMC to Schedule 40- can that be buried in concrete?
Any help clarifying if I CAN encase the fitting in concrete- or article showing why I can't- would be greatly appreciated.