Though indirectly, likely yes.Transmission lines on a tower say 200 kv have grounded lines above them do the grounded lines end up touching the ground rod at my home ?
Those are shield or static wires
lightening protection and they are grounded (obviously)
but usually not a I carrying conductor, ie neutral
eg
delta transmission w/shields to a local distribution substation
delta-wye transformer with a derived neutral
statics tied to station bed
so is the neutral
sometimes the neut will have a small Z to drop any gnd bed potential rise due to a fault or lightening strike
but often no grounding Z since the bed is so effective that it holds 0 potential even under a fault/lightening strike
so yes tied together indirectly thru earth
but no, little risk of it flowing I into loads
Llightening will flow seeking equi-potential, so it does not 'seek' your system
a phase fault will tend to return to the power source which is not your home
bigger risk of a phase lightening strike bringing problems in to the load
Are you saying that the static wires don't carry ground current?
what is 'ground current'?
ground fault?
capacitive coupling?
delta or wye transmission?
Yes, Ground fault.
delta, single line to ground, no
wye, yes, in parallel with earth, although it may not be terminated at the X0 if a separate neutral is carried so would carry it for a ways then shunt to ground to the X0
I don't often see pure delta config (un-grounded) transmission systems. The ground fault current typically has to come from somewhere. If not, then all insulation has to be L-L rated as well as the surge arrestors. I also don't typically see the neutral carried directly to anywhere unless its a dedicated industrial customer. Typically, the X0 or H0/X0 (autobanks) terminals are grounded to the mat along with the static wires. Is that not the case where you're at?
So, for ground connected loads, most imbalance would cause ground current to flow over the static wires. The imbalance could be from imbalanced loads or a fault.
PA
most lines that serve mine substations are delta with static lines, no other loads are served off of these (usually)
25-69kv range
if they are wye (connected delta to the mine xfmr primary with a wye high resistance grounded secondary, 15-25 A) they have the static lines up high and will carry a 4th conductor below the phases, only the static line is landed on our mat
Gotcha...that makes sense now. I'm used to dealing with HV & EHV autobanks and highside g-wye distribution banks. Don't ask me why the utility g-wyes the highside of a distribution bank, it is very hard to coordinate with a ground source in the middle of a T-line.
our primary concern is isolation
not taking a utility fault/strike into the mine for 2 reasons
1 shock-raising frame/touch potential
2 ignition source for methane
we use 2 beds and both must be <2 ohm
the sub is set on one, station or primary bed
the second is a min of 50' away inline with the mine, neut or safety bed
electrically isolated but there is unavoidable coupling thru earth
the ngr high side is connected to the X0 and the low side is connected to the neut bed and used as the mine ground
no single phase loads allowed w/o a xfmr
so most 138/345/etc kv transmission lines are wye-wye from step up to dist xfmr?
and the shield/static carries the imbalance?
interesting
I would have thougt delta-delta with the gen end step-up being a Z gnd primary and the distribution end secondary being wye-n/g so single phase loads could be derived
learn something new every day
thanks
Most 345/115 or 345/230 or 500/230 subs have auto banks that are g-wye on both high side and low side. Distribution subs are often power xfmrs that are g-wye on high side and low side. Generator buses are typically z gnd and connected delta to the step-up and then g-wye on the high side (transmission side).
Transmission lines on a tower say 200 kv have grounded lines above them do the grounded lines end up touching the ground rod at my home ?
I don't often see pure delta config (un-grounded) transmission systems. The ground fault current typically has to come from somewhere. If not, then all insulation has to be L-L rated as well as the surge arrestors. I also don't typically see the neutral carried directly to anywhere unless its a dedicated industrial customer. Typically, the X0 or H0/X0 (autobanks) terminals are grounded to the mat along with the static wires. Is that not the case where you're at?
So, for ground connected loads, most imbalance would cause ground current to flow over the static wires. The imbalance could be from imbalanced loads or a fault.
Most 345/115 or 345/230 or 500/230 subs have auto banks that are g-wye on both high side and low side. Distribution subs are often power xfmrs that are g-wye on high side and low side. Generator buses are typically z gnd and connected delta to the step-up and then g-wye on the high side (transmission side).
But you still need to have a line to neutral load connected before there is any current on the neutral. Transmission voltages typically have no load connections to the neutral, but I suppose there could be neutral if wye connected primary side of any transformers supplied has a connection to neutral, but a floating primary neutral or delta primary transformers will not have any connection to neutral.Thanks
in that case the shield is a current carrying conductor under nml conditions
carries imbalance
Not in my area though. What would be the benefit of wye-wye at 115kv to 13.8kv? :blink: Around here generation step up is delta wye-gr (22kv to 345kv); wye-gr auto with a delta territory (345kv to 115kv) distribution delta wye-gr (115kv to either 13.8 or 23kv) and utilization wye-gr wye-gr (13.8 to either 120/208 or 277/480).
But technically even with un-blanced loads the ground current is small as the 115kv to 13.8kv transformers are delta wye. Any neutral current on the secondary is transferred to the phases as zero sequence currents do not pass.