Trash Compactor / Disconnect

Status
Not open for further replies.

jmd445

Senior Member
Is there anywhere in the code specifying the location of the main service disconnect as well as the operating controls for a hydraulically operated commercial trash compactor?

Jim
 

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
Re: Trash Compactor / Disconnect

Yes it would follow the general rules in Art 110 and 240, specifically 110.16, 110.26 and 230.70
 

jmd445

Senior Member
Re: Trash Compactor / Disconnect

Maybe I wasn't clear......I was refering to the disconnect for the compactor not the building service disconnect.

Jim
 

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
Re: Trash Compactor / Disconnect

Yes. See 110.26 and 110.16. For a motor load see 430.102 (A) and (B). You need a disconnect within sight of the motor and motor controller. this may be two disconnects. One is required to be readily accessbile and the other is accessible.
 