My mom had a new Travis Industries gas fireplace insert installed. I extended the living room circuit to connect to the insert. The house was recently rewired and outfitted with AFCI/GFCI circuit breakers. When I connected to the insert, the breaker tripped. Initially, I thought there might be a problem with the insert. I inspected the field connection (made by the insert installer) and it looked correct. (hot, neutral, ground). When I checked for continuity, I found the ground and neutral had continuity. Which I believe caused the circuit breaker to trip. I spoke with the heating company and they asked me to email my concerns to them and they would contact the factory. Since then, I took it off of a AFCI/GFCI breaker and installed on an AFCI breaker. It works in this mode. I continue to ask the manufacture for some response in why the neutral and ground and connected together at the unit. But I haven't received a reply.
I haven't stayed current with electrical code so for those of you have knowledge in this area. Question: Are manufacturers allowed to connect the ground and neutral in their appliances? Seems like there are exceptions for specific applications. This installation is in Oregon.
Thanks for any insights.
I haven't stayed current with electrical code so for those of you have knowledge in this area. Question: Are manufacturers allowed to connect the ground and neutral in their appliances? Seems like there are exceptions for specific applications. This installation is in Oregon.
Thanks for any insights.