What is best practice for terminating the ground wires within tray cable? Especially when you have a parallel tray cable feeder?
For example: A parallel tray cable feeder is installed in cable tray to a 400 amp distribution panel. At the panel, the cable is installed in conduit(s) for the vertical drop.
- 2 x #3/0-3C THHN-PVC Tray Cables with Ground are used. (The cable contains 4x interstitial ground wires, with a combined equivalent of 4 AWG)
- The cable(s)'s interstitial ground wires do not meet the ampacity requirement (Table 250.122) for the parallel installation, so a bare copper ground is installed in the cable tray sized to the largest OCPD that will be present in the tray (250.122(c)). Let's say 1200 amps, so #3/0 bare copper. At the vertical drops, a #3 insulated wire is split bolted onto the #3/0 and run with the tray cable in each separate conduit down to the panel.
In the panel: you now have 2x #3 ground wires, plus the 8x interstitial ground wires from the tray cable. This appears to be what is permitted under 250.122(f).
My questions is: What is the best practice for complying with 250.122(f)(2)(c)?
"If multiconductor cables are paralleled in the same raceway, auxiliary gutter, or cable tray, a single equipment grounding conductor that is sized in accordance with 250.122 shall be permitted in combination with the equipment grounding conductors provided within the multiconductor cables and shall all be connected together."
(2023 NFPA 70)
- Split bolts only allow 2-3 conductors, and most ground terminals in the panel allow 1 conductor.
- Following these rules, for the 10 ground wires, would you use split bolts (or similar lug/connector) to combine 2-3 ground wires until they are reduced to the number of terminals you have available? (This is my general method, just wondering if anyone has encountered a better solution.)
For example: A parallel tray cable feeder is installed in cable tray to a 400 amp distribution panel. At the panel, the cable is installed in conduit(s) for the vertical drop.
- 2 x #3/0-3C THHN-PVC Tray Cables with Ground are used. (The cable contains 4x interstitial ground wires, with a combined equivalent of 4 AWG)
- The cable(s)'s interstitial ground wires do not meet the ampacity requirement (Table 250.122) for the parallel installation, so a bare copper ground is installed in the cable tray sized to the largest OCPD that will be present in the tray (250.122(c)). Let's say 1200 amps, so #3/0 bare copper. At the vertical drops, a #3 insulated wire is split bolted onto the #3/0 and run with the tray cable in each separate conduit down to the panel.
In the panel: you now have 2x #3 ground wires, plus the 8x interstitial ground wires from the tray cable. This appears to be what is permitted under 250.122(f).
My questions is: What is the best practice for complying with 250.122(f)(2)(c)?
"If multiconductor cables are paralleled in the same raceway, auxiliary gutter, or cable tray, a single equipment grounding conductor that is sized in accordance with 250.122 shall be permitted in combination with the equipment grounding conductors provided within the multiconductor cables and shall all be connected together."
(2023 NFPA 70)
- Split bolts only allow 2-3 conductors, and most ground terminals in the panel allow 1 conductor.
- Following these rules, for the 10 ground wires, would you use split bolts (or similar lug/connector) to combine 2-3 ground wires until they are reduced to the number of terminals you have available? (This is my general method, just wondering if anyone has encountered a better solution.)