Is this correct? I’m out of town and don’t have my code book with me with my notes pertaining to this.
Situation-pulling (tray cable) branch circuit conductors to a splice box for lighting and receps. Raceway is mostly cable tray, so using TC and engineers have upsized conductors to number #8 for voltage drop. (208v) 20amp OCPD.
Are my calculations correct? We have a 3c #8 cable with #10egc. From my math is seems we need to use the 3rd spare conductor as the EGC since the original is not upsized proportionally to the-ungrounded and grounded conductors.
#12-6,530cm
#8-16,510cm
16,510/6,530=2.52
Original egc size #12 per OCPD multiplied using 2.52 shows the EGC would also need to be a #8.
#12-6,530 x 2.53= 16,455cm. Next size up is #8awg.
Conclusion-spare original green #10wire in cable and use the available 3rd #8as the proportionally sized EGC.
Situation-pulling (tray cable) branch circuit conductors to a splice box for lighting and receps. Raceway is mostly cable tray, so using TC and engineers have upsized conductors to number #8 for voltage drop. (208v) 20amp OCPD.
Are my calculations correct? We have a 3c #8 cable with #10egc. From my math is seems we need to use the 3rd spare conductor as the EGC since the original is not upsized proportionally to the-ungrounded and grounded conductors.
#12-6,530cm
#8-16,510cm
16,510/6,530=2.52
Original egc size #12 per OCPD multiplied using 2.52 shows the EGC would also need to be a #8.
#12-6,530 x 2.53= 16,455cm. Next size up is #8awg.
Conclusion-spare original green #10wire in cable and use the available 3rd #8as the proportionally sized EGC.