Tray Cable
george t. everett
New York
My local supply houses (3) are selling 8/3 & 6/3tray cable for direct buial to feed residenial out buildings, such as detached garages & pool houses. This cable consists of 3 black conductors, numbered 1,2&3, and a ground. I told them that this is a code violation because the neutral has to be white. They said they have had no complaints. Any comments? What is the primary use for this cable?
tom baker
Bremerton, Washington
Master Electrician
Re: Tray Cable
Tray cable is most often used in cable trays. (I edited my reply I didn't want to sound smart, but thats the most common application). I use thousands of feet of power limited tray cable, which is 300 volt rated. ...A black or other color conductor can be reidentified as a grounded conductor if its larger than 6 or 4 awg. The wholesale houses don't really care about code, just sales. A violation from an AHJ on an installation would get their attention.
[ July 08, 2003, 10:52 PM: Message edited by: tom baker ]
don_resqcapt19
Illinois
retired electrician
Re: Tray Cable
Tom,
Most tray cable that I have seen is identified for direct burial use and this is permitted in 336.12(4). The only real issue is the re-identification of the conductor that is being used as the grounded conductor. Exception #1 to 200.3(E) limits the re-identification to occupancies where the conditions of maintenance and supervision ensure that only qualified persons service the installation. This would limit the use in a dwelling unit.
Do they make TC cable with a white conductor? I've never seen it.
Don
tom baker
Master Electrician
Re: Tray Cable
Good question, I 'll check in my Belden catalog. They have several color codes one of which may be white black red...
Perhaps the mgf has an overstock of this type cable. 3 blacks?
tom baker
Master Electrician
Re: Tray Cable
Good morning all. In the belden catalog it shows 3 different color codes for tray cable
K-1 is blk, wht, red, green, etc
K-2 is blk, red, blue
method 4 is all conductors are black, and numbered.
What I buy is K-2.