Tray Rated Cable in Conduit

Status
Not open for further replies.

Droid

Member
Location
Rochester
Occupation
Electrical Project Manager, QA/QC
I'm getting conflicting direction regarding the installation of tray rated (TC) cable installed in conduit. Please point me to the specific Article covering this topic. I appreciate your reply. Thank you.
 
336.10(3) allows it to be installed in raceways
The Notes to Table 1 Chapter 9 address fill calculations
 
I'm getting conflicting direction regarding the installation of tray rated (TC) cable installed in conduit. Please point me to the specific Article covering this topic. I appreciate your reply. Thank you.
You need to be careful with jam factor while pulling. The flat tray cable that is basically the same cross section as 14-2 or 12-2 romex will jam in your bends if you try to pull multiple cables in one conduit
 