Reggie Reg
New member
- Location
- Florida
I am helping troubleshoot a gym that has numerous treadmills in it. Too often, the motor controller boards give up the ghost. The mfg recommends a dedicated circuit (hot/neutral/ground) and a 20a bkr for each treadmill receptacle (115V, single phase). Unfortunately, the gym came before the equipment and the receptacle does not have the recommended arrangement (i.e. grounds and neutral are not dedicated to each receptacle only--they tie together before returning to panel) Here are the observations at the three phase panel that feeds the receptacles:
*Neutral current is higher than phase currents
*4% voltage distortion (THD)
*80 - 100% current distortion (THD)
How would the dedicated grounds and neutral help the current and voltage distortion. Any suggestions on plug in devices at the receptacles that could help.
*Neutral current is higher than phase currents
*4% voltage distortion (THD)
*80 - 100% current distortion (THD)
How would the dedicated grounds and neutral help the current and voltage distortion. Any suggestions on plug in devices at the receptacles that could help.