Normally, on a college campus, I treat the "feeder" to the building from the pad mounted transformer like any other feeder from a transformer; i.e. 3 phase, neutral and SSBJ.
The state inspector who oversees this particular school recently informed me that as per 225.36, you could essentially treat this feeder the same way you would treat the service conductors comming in from a utility pad mount. I.e. 3 phase and instead of a Grounded Service Conductor, just a "grounded conductor".
So you bond at the main disconnect and the main disconnect needs to be UL listed for service entrance.
My question is this, whether it's a service or a feeder to a primary metered campus building, what color coding should the Grounded Conductor and Grounded Service Conductor be. Green? White? Gray" or none of the above.
The state inspector who oversees this particular school recently informed me that as per 225.36, you could essentially treat this feeder the same way you would treat the service conductors comming in from a utility pad mount. I.e. 3 phase and instead of a Grounded Service Conductor, just a "grounded conductor".
So you bond at the main disconnect and the main disconnect needs to be UL listed for service entrance.
My question is this, whether it's a service or a feeder to a primary metered campus building, what color coding should the Grounded Conductor and Grounded Service Conductor be. Green? White? Gray" or none of the above.