Boxes located about 20 feet above grade.....cables draped through the tree limbs to spot lights - can see them if you zoom in on photo. Am I correct to be concerned about access to the boxes and general wire supports? Thanks
 

Attachments

  • DSCF5344.jpg
    DSCF5344.jpg
    153.4 KB · Views: 0
  • DSCF5343.jpg
    DSCF5343.jpg
    158.5 KB · Views: 0

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
If you didn't do it I would not mess with it. Sure it is a violation, however, do you really want to mess with it and stapling it will probably be worse as the tree grows.
 

Fnewman

Senior Member
Location
Dublin, GA
Occupation
Sr. Electrical Engineering Manager at Larson Engineering
Almost all landscape lighting is low voltage. Those boxes in the picture look like LV transformers, but hard to tell.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
It is permitted to install lighting in trees and attach the wiring directly to the tree, you just cannot span from one live tree to another.
 