arezapour2004
Member
- Location
- Houston, TX
- Occupation
- Associate Electrical Engineer
We are evaluating the ampacity basis for installing 15 kV, MV-105, single-conductor 750 kcmil copper cables in a Trenwa precast concrete trench system and would appreciate your guidance on the appropriate NEC-compliant methodology.
Specifically, we seek clarification on the following:
Applicable NEC references:
Effect of trench configuration:
Engineering calculation requirement:
Your guidance will help us establish a defensible, code-compliant ampacity basis for this installation.
Specifically, we seek clarification on the following:
Applicable NEC references:
- Which NEC 2023 provisions govern ampacity determination for medium-voltage conductors (>2000 V) installed in a concrete trench system such as Trenwa?
- Is this installation eligible to be treated as “free air,” similar to Table 315.60 C (3) free-air assumptions, or must it be evaluated using engineering methods per current NEC requirements?
- How does the presence of a solid cover, ventilated cover, or no cover (open trench) impact the ampacity basis and classification (free air vs. enclosed installation)?
- Is it acceptable to start with a 105 °C free-air ampacity of approximately 990 A for 750 kcmil Cu and apply adjustment factors such as:
- 0.70 per NEC 392.80(B)(1) for cable-tray grouping, and
- 0.95 for 40 °C ambient temperature,
- Does NEC-2023 require a formal engineering thermal analysis (e.g., Neher-McGrath / ICEA) for MV cables installed in covered or partially covered Trenwa trench systems, and if so, should this be the governing design approach?