linwue said:I was just wondering if you can use tri-plex or "use cable" for an overhead service,in pvc up to the weatherhead?
Ask him what should be used for an overhead run to a separate building.dnem said:That same inspector that fails the USE that peeks inside, has also said that triplex has no UL listing of any kind and can only be used by the power company. He fails any contractor that uses it for anything.
I've been meaning to find out if he's right. If he is, then the stuff is installed illegally all over the place in my area in Ohio. Everybody uses it on overheads whether they're with the power company or not.
Minuteman said:I know that our inspectors will not pass a riser (or mast) that has a bare neutral.
LarryFine said:Ask him what should be used for an overhead run to a separate building.
infinity said:What Article do they cite?
It's also not his jobto be so evasive as to repeatedly say "Failed; try again." so we don't have to try several times.iwire said:That is not the inspectors job to tell us how to do our job.![]()
LarryFine said:It's also not his jobto be so evasive as to repeatedly say "Failed; try again." so we don't have to try several times.
Mayhaps I should have said "What would he deem acceptable?"
LarryFine said:Ask him what should be used for an overhead run to a separate building.
iwire said:That is not the inspectors job to tell us how to do our job.
LarryFine said:It's also not his jobto be so evasive as to repeatedly say "Failed; try again." so we don't have to try several times.
Mayhaps I should have said "What would he deem acceptable?"
iwire said:Larry I don't understand.
It is not the inspectors job and to explain how the work should be done.
IMO they are going out on a limb if they are doing much more than hinting what they would like to see.
kingpb said:Maybe someone can answer this, if it's off topic I will start a new one.
Here in xxx, FL (name removed to avoid conflict) the local utility is running SE cable, attaching it directly to the house, on the way to the meter. then the Contractor is being allowed to run SE, attached to the house, no conduit or protection, to go from the meter base to the panel, located somewhere inside the residence.
I have seen where they attach the overhead conductors to the back of the house, off the ally, then run SE cable under the eaves, and around to the side of the house into the meter.
What article(s) in the NEC are allowing this? I have a hard time believing that this is deemed acceptable, having exposed "Romex" essentially, and yet they are going to require AFCI for every circuit in a house? Where is the logic. These are 100A circuits we are talking about.
Alright, someone please splane..................
iwire said:That is not the inspectors job to tell us how to do our job.
Typical triplex is not listed and is not marked at all, it creates a number of violations when used for NEC installations.
Have I used it?
Yes.
kingpb said:Maybe someone can answer this, if it's off topic I will start a new one.
Here in xxx, FL (name removed to avoid conflict) the local utility is running SE cable, attaching it directly to the house, on the way to the meter. then the Contractor is being allowed to run SE, attached to the house, no conduit or protection, to go from the meter base to the panel, located somewhere inside the residence.
hillbilly said:SE cable is just what the initials imply...Service Entry Cable.
Down south, you will see a lot of installations like you describe.
That sheds some light on my misunderstanding. Around here we call the service drop cable that the POCO uses with the 2 insulated Aluminum and one bare conductors, "triplex". The underground we use is type URD.hillbilly said:iwire...I know that we've had this discussion before about "Triplex" cable.
So, just to clarify for the readers, down south (USA), what we call "Triplex" cable is 3 spirally wound conductors with each conductor having a X linked polyethylene outer covering. It is rated USE or USE-2 and has a cross rating of RHH (I think that's the correct rating), anyway it's cross rated to allow use inside a building.
The service drop cable that the POCO uses is 2 insulated and one bare conductors, also spirally wound. I have no idea what the rating is. It's just called "service drop cable" around here.
If you do a web search for "Southwire" you will find a company that produces the Triplex cable that I describe. I don't know if "Triplex" is a trademark name or not.
So anyway, around here, the OP could run "Triplex" in conduit or direct buried, inside or outside.
steve
dnem said:Up north in Ohio it's the same thing. 70 to 80 % of all services are SE without conduit protection. The only place the SE can't be run openly is where it is subject to vehicle damage such as areas where a driveway comes right up along side of a section of the house and the service conductors are run in that area.
David
Hi, guess I should add my two pesos worth here, we have a local utility that asked me if triplex was ok in a riser, I said, " I dunno" he was satisfied, and made the connection... But the price of Copper wire has gone up so high,that small pieces of URD, and triplex laying around that would make riser wire, are really looking good right now, and I'm tempted to try.... Knowing our local inspectors, Im sure this will cause havoc, had the "CHEEF" inspector give me a corrections notice for not forming a drip loop in the feeders extending from a weatherhead, an item the utility does when they make the hook-up. Wonder what he would have done if the riser had URD or USE or triplex in it???? If we could get a determination, sure would save some cash on the installation, and give us a use for the left over small pieces of service wires we all have laying around.... Dennis in NMLarryFine said:It's also not his jobto be so evasive as to repeatedly say "Failed; try again." so we don't have to try several times.
Mayhaps I should have said "What would he deem acceptable?"