Triad Grounding
Triad Grounding
Hello to all,
Triad grounding is important in order to facilitate periodic testing of the effective grounding system. Three rods are buried and connected with insulated cable (probably 90 mm), ofcourse the insulation of that part of the cable which is bolted to the rod is removed. Test pits allowing access to the top of each rod.
In order to effectively test the ground resistance the rest of the grounding system must be disconnected from the rod, if only a single rod was buried then for the duration of the test the system would be ungrounded which is extremely dangerous, the three rods and their interconnections allow this testing to occur and also eliminate the need for a test rod to be driven as 2 out of the 3 rods can be disconnected and the earth resistance test done while the third rod maintains an effective ground. The distance between the rods is usually equal to or a bit more than the length of the rod in order to avoid interference and thus provide a true measurement of the earth resistance at that point. This system also facilitates redundancy and increased availability of the grounding system and is used mainly for grounding of instrumentation and computerized systems and so is isolated (except for a single bond) from the plant (dirty) earthing network which may be buried bare copper, rods and building rebar etc.