451F
Member
What are possible sources for a triangle waveform between pipes in a residential neighborhood? The frequency was ~60 HZ. (59.63)
Arcing has perforated a copper pipe that was touching a steel drain pipe. There is about 1 volt difference between the pipes now as measured on the Low Z setting on a Fluke 117 DMM. The copper pipe tested as bonded to the building electrical system.
The steel drain is connected to the sinks with plastic traps so there is not the usual short between drains and copper.
The voltage difference varied over time with no relationship to equipment cycling in the building.
Thanks in advance for your time and comments.