At present I'm specificly wondering about Single-Family Residential where the existing has non-grounded receptacles (2pronged-Black/White no Green or bare copper) and the work would be running grounded conductors for each affected Breaker from the panel ground bus to New Grounded receptacles (3pronged grounded).
My question being would this work require that the Breaker or Panel or any affected systems other than the receptacles involved be "brought up to Code"?
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Welcome to the forum.

Check with our local building authority.

Here, if you renovate 50% or more by floor area, present code applies.
 

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
There are a few requirements that are not subject to grandfathering, examples replacement receptacles must comply with current code for WR, TR, GFCI, AFCI. Panel schedules have to be current, service fault current calcs.
 

rc/retired

Senior Member
Location
Bellvue, Colorado
Occupation
Master Electrician/Inspector retired
There are a few requirements that are not subject to grandfathering, examples replacement receptacles must comply with current code for WR, TR, GFCI, AFCI. Panel schedules have to be current, service fault current calcs.
I agree. Truth be told, I hate the term "grandfather".

Ron
 