Iconclass
New member
- Location
- Manassas, Va, Prince William County
Prime example of GE engineers and the local AHJ not understanding the basics of Kirchoff's current law when it come to the NEC on grounding.. I have a double ended service with a three pole secondary tie breaker. The service also includes a generator tap on one end of the tie point on the load side. The secondary tie breaker is a three pole unit. The system has a continuous solid neutral bus between the two service points which are at different ends of the service. There are two Main bonding jumpers installed at both ends of the service. There exist a generator tap which is on the load side of the service via bus duct which also has a main bonding jumper installed. With the three main bonding jumpers installed there is a division of current according to Kirchoff which is a violation of 250.6 (A) (B) which clearly states no objectionable can flow. The way GE set up the service is that current can flow on the main bonding jumpers in the system. This is a 480 three phase four system at 4,000 amps on each end of the tie. The MBJ is not rated for 4,000 amp as the neutral bus is but is paralleling the load through it via triple MBJ's. This is a hospital installation.