Anyone have a figure for the resistance of 2/0 AL triplex. I'm noting a 20vac drop over approx 750' of a mains run. I'm pretty confident I have an issue, but curious the impact resistance may have assuming the wire is fully intact.

THANKS
 
This does not appear to be a how to question, so I have approved it.
I don't see why you can't take the resistance from Table 8, in Chapter 9 to do the calculation.
 
TY. Don't have access to NEC in Belize, but your ref's allowed a web search to locate the table. THX again
While not very user friendly, you can view the NEC for free at the NFPA website. You do have to register with an email address. nfpa.org/70 then click on "free access".
 