hhsting
Senior Member
- Location
- Glen bunie, md, us
- Occupation
- Junior plan reviewer
I have plans that show one feeder breaker from panelboard sized 200A with one feeder that feeds control panel which feeds 3 separate 10HP 208V three phase triplex booster pumps.
I am not sure if control panel has OCPD and overload for each of the pumps or not. Its at plan review stage
Question:
1. Assuming the control panel does NOT have OCPD and overload how would one size the feeder breaker for all three pumps?
2. Assume the control panel does have OCPD and overload. Using 430.62 10HP has fla of 30.8A. 30.8ax2.5=77A. So next size up is 80A. So now I add 80+30.8+30.8=141.6A. So the feeder breaker size should be 125A not sure how to get 200A? Does anyone know?
I am not sure if control panel has OCPD and overload for each of the pumps or not. Its at plan review stage
Question:
1. Assuming the control panel does NOT have OCPD and overload how would one size the feeder breaker for all three pumps?
2. Assume the control panel does have OCPD and overload. Using 430.62 10HP has fla of 30.8A. 30.8ax2.5=77A. So next size up is 80A. So now I add 80+30.8+30.8=141.6A. So the feeder breaker size should be 125A not sure how to get 200A? Does anyone know?