Triplex Sub panel
Castrovinci
NJ
All,
I am running an outdoor 100A 120v Three phase sub panel for some truck heaters. I need to do an overhead run of about 200'. I am going back and forth on cost and options of stepping it up to 480 and step back down or just upsizing the wire for voltage drop.
Here is my issue....
Can i run triplex for the subpanel and just run two ground rods outside or do I have to run a quadplex so I also have a ground and neutral? If I can run the triplex I saw somewhere in the forum someones state would not allow the grounded and grounding conductor to be one even though it appeared NEC allows it for a seperate building. I am thinking this can be treated as a seperate building even thought the panel is going to mount on a telephone pole outside in the yard and its not in a building?
If I use a step up and then step back down I can get away with the triplex since my high voltage side does not require a neutral? Downside is a lot more money and labor involved. I am hoping the first option is possible.
250.32, the applicable section, applies to buildings OR STRUCTURES.
The NEC Definition of a structure is "That which is built or constructed".
Most NEC folks would look at your pole/panel/etc as a structure and enforce 250.32 requiring a separate EGC.
I do not think you need to run a neutral if it is not being used. You do need to run a green wire out there with the 3 power wires.
Thank you
Thank you
(1) Equipment Grounding Conductor. An equipment grounding conductor as described in 250.118 shall be run with the supply conductors and connected to the building or structure disconnecting means and to the grounding electrode(s). The equipment grounding conductor shall be used for grounding or bonding of equipment, structures, or frames required to be grounded or bonded. The equipment grounding conductor shall be sized in accordance with 250.122. Any installed grounded conductor shall not be connected to the equipment grounding conductor or to the grounding electrode(s).
That about sums it up! Thanks.
All,
I think you need more than triplex... If this is 3 phase and you need 120V and all three phases, you need 4 insulated wires plus a grounding conductor. Does anyone make pentaplex?
Not sure that all the work in transforming the voltage will save you enough in the end, but maybe. If you can make everything 208V and not require a neutral, perhaps the amp loading will be less?
Yes, my original post should of said quadplex:slaphead: and not triplex sorry about that. They don't make anything higher than the quad so no (Pentaplex or a sexaplex:lol:) (according to the supply house) that is why I was trying to just do the three conductors and a neutral and see if there was an exception to ground at the panel and not need an additional wire, but there is not. My only option is if I am going to use two transformers I can then use the quadplex. Trenching is not an option unless the facility wants to front the 30K cost to dig and repair.:jawdrop:
I doubt anyone is still that far behind, but note that (i think) 2005 and prior you could "rebond" the neutral at a remote structure. Assuming you are on a cycle later than that, note that triplex and quadplex is not the only option for overhead. The code does permit most wiring methods to be run as messenger supported wiring. This means you could take 4 plus ground SER or MC and fasten it to your own messenger. Seems a little mongrel I know but it is permitted.
Yes, you could as long as there were no metallic connections between the structures.
Done that using TC but it was only to three way some lights.
All,
Looks like you said what you meant in the OP.:p
It needs separate grounded and grounding conductors whether it is a separate structure or not if the applicable code is 2005 or later.
You could consider not stepping voltage up and save the cost of one transformer, and just install a 1:1 ratio transformer at the load end with a neutral on the derived conductors.
I have to do a little thinking on this, but it may also be possible to derive a neutral using autotransformers, and they wouldn't need to be as large as a separately derived unit would be. Keeping load balanced would be the biggest trick to keeping them smaller though.