I get a queasy feeling sizing triplex feeder runs on poles.
Question does existing #6 AL triplex identified as XLPE and run in free air on poles utility style violate NEC on 90A breaker? Mast conductors are 1/0 AL XHHW-2.
Neutral meets 250.32(B)(1)Exception
Art 100 defined covered conductor.
XLPE not recognized by code = covered.
ART 225.4 permits outside feeders to be covered.
Table 396.10 A permits other factory assembled power cable identified for the use.
ART 100 defines Identified. Triplex is Identified for the use.
MFR has it tested is used by utilities all the time.
Table 310.15(B)21 Covered conductors in free air.
#6 AWG = 101A
110.3(B) Have to use mfr instructions
MFG ampacity table states "COLLIE"
6awg XLPE = 85A
240.4(B) Next size up = 90A
Link to MFR instructions.
http://www.cable.alcan.com/NR/rdonl...1/0/MultiplexOverheadServiceCableBrochure.pdf
Question does existing #6 AL triplex identified as XLPE and run in free air on poles utility style violate NEC on 90A breaker? Mast conductors are 1/0 AL XHHW-2.
Neutral meets 250.32(B)(1)Exception
Art 100 defined covered conductor.
XLPE not recognized by code = covered.
ART 225.4 permits outside feeders to be covered.
Table 396.10 A permits other factory assembled power cable identified for the use.
ART 100 defines Identified. Triplex is Identified for the use.
MFR has it tested is used by utilities all the time.
Table 310.15(B)21 Covered conductors in free air.
#6 AWG = 101A
110.3(B) Have to use mfr instructions
MFG ampacity table states "COLLIE"
6awg XLPE = 85A
240.4(B) Next size up = 90A
Link to MFR instructions.
http://www.cable.alcan.com/NR/rdonl...1/0/MultiplexOverheadServiceCableBrochure.pdf