A anbm Senior Member Location TX Occupation Designer Jul 14, 2009 #1 Does the code requires to drive grounding rod at a specific location? i.e.: under main service entrance elecical room, inside foundation of building, outside foundation of building? Any recommendations guys? Thanks!
Does the code requires to drive grounding rod at a specific location? i.e.: under main service entrance elecical room, inside foundation of building, outside foundation of building? Any recommendations guys? Thanks!
B bphgravity Senior Member Location Florida Jul 14, 2009 #2 No. The code is rather silent on the specific location that ground rods must or should be placed. See 250.53(A) and (G) for some key requirements. Since ground rods service such a minor purpose, I would spend too much time worrying about this...
No. The code is rather silent on the specific location that ground rods must or should be placed. See 250.53(A) and (G) for some key requirements. Since ground rods service such a minor purpose, I would spend too much time worrying about this...
electricmanscott Senior Member Location Boston, MA Occupation Massachusetts Master Electrician, one man show. Jul 14, 2009 #3 No locations are specified but it must be driven below the permanent moisture level. Of course only where practicable.
No locations are specified but it must be driven below the permanent moisture level. Of course only where practicable.
D Doug S. Senior Member Location West Michigan Jul 14, 2009 #4 electricmanscott said: No locations are specified but it must be driven below the permanent moisture level. Of course only where practicable. Click to expand... Huh? Sorry, I found it 250.53(A) '05 Code. I just don't remember reading that before. Last edited: Jul 14, 2009
electricmanscott said: No locations are specified but it must be driven below the permanent moisture level. Of course only where practicable. Click to expand... Huh? Sorry, I found it 250.53(A) '05 Code. I just don't remember reading that before.