Tripod grounding rod - driven location

Status
Not open for further replies.

anbm

Senior Member
Does the code requires to drive grounding rod at a specific location?

i.e.: under main service entrance elecical room, inside foundation of building, outside foundation of building? Any recommendations guys? Thanks!
 

bphgravity

Senior Member
Location
Florida
No. The code is rather silent on the specific location that ground rods must or should be placed. See 250.53(A) and (G) for some key requirements.

Since ground rods service such a minor purpose, I would spend too much time worrying about this...
 