treyp3
Member
- Location
- Fernandina Beach Fl
Had a call from a landlord today, 15 amp arc fault breaker tripping, flat screen TV fried. Tenant says breaker trips once a week for the year she has been there. Last night it tripped and she reset it, then noticed TV smoking. She unplugs the TV and the breaker trips 5 more times. Working fine when I got there.Checked 3 way switches for shared neutrals, checked connections at breaker, pulled receptacles, amp probed circuit at panel. She doesn't notice any pattern to the tripping (like when she uses the vaccum). Pluged in a bunch of stuff, got it up to 22 amps before it tripped. Left the circuit pulling about 10 amps for about 2 hours and still no tripping (whent out to get a 15a Sq D QO arc fault and took a long lunch). I replaced the arc fault breaker and left the TV unplugged. I felt that maybe the TV was going bad and was the culprit all along. The new breaker held for about six hours and tripped again. I cant figure what would fry a TV and not trip for for 6 hours. I told her todays fix may not repair the problem but that it was a good start. Now I have to go back tomorrow, any suggestions where to start?