Djglennon62
Member
- Location
- Dubuque, Iowa
I have a 60A 3 phase breaker feeding 2 50A 3 phase breakers, that are protecting 2 sewage pumps, that operate alternately. What would cause the 60A breaker to trip before the 50A breaker?
The trip curves are so close it’s a horse race. A different 60 or 50 may change which one trips first.I have a 60A 3 phase breaker feeding 2 50A 3 phase breakers, that are protecting 2 sewage pumps, that operate alternately. What would cause the 60A breaker to trip before the 50A breaker?
The trip curves are so close it’s a horse race..
He said it's on an alternator, so (presumably) only one at a time .3ph 60A sees 2 pumps, or two 1ph 50A breakers see 1 pump each
3ph 60A sees 2 pumps, or two 1ph 50A breakers see 1 pump each
He said it's on an alternator, so (presumably) only one at a time .
But this brings up another point, in that if Pump #1 is running for a long time, the 60A breaker thermal sensing elements have been "seeing" that pump current the whole time. Pump #1 shuts down and if Pump #2 starts up almost immediately, the 60A breaker thermal sensing elements are still hot because of running Pump #1, then it has to deal with the starting current of Pump #2. The 50A breaker for Pump #2 however is cold because it has been doing doodley-squat the whole time Pump #1 was running. The starting current for Pump #2 is no problem for it yet that starting current for Pump #2 is ADDED onto the thermal state of the 60A breaker, so it trips but not the 50A breaker.
I have a 60A 3 phase breaker feeding 2 50A 3 phase breakers, that are protecting 2 sewage pumps, that operate alternately. What would cause the 60A breaker to trip before the 50A breaker?
..if Pump #2 starts up almost immediately, the 60A breaker thermal sensing elements are still hot because of running Pump #1, then it has to deal with the starting current of Pump #2..
There are also facilities that have age on them and maybe when equipment has failed didn't get replaced with identical components to what was originally there. Then there is sometimes the maintenance guy/operator that changes things thinking his idea is better than what was there before.Just my take on why I would be looking for an operational or maintenance problem versus electrical... the waste water plants I worked at were designed by ch2m Hill or other large engineering firms. The capital cost of these plants can exceed 9 figures, and the electrical systems are usually spot on. Unless the pumps were changed, or the electrical was done in-house, I find it unlikely that the design is wrong.
There could be an issue with ultrasonic level indicators or float switches causing rapid cycling, and the 60 amp breaker would already be warm and possible trip when the other pump comes on.
I agree that we need more information from the original poster, such as do both pumps ever run at the same time, how many starts per hour, amperage readings, etcetera
Just my take on why I would be looking for an operational or maintenance problem versus electrical... the waste water plants I worked at were designed by ch2m Hill or other large engineering firms. The capital cost of these plants can exceed 9 figures, and the electrical systems are usually spot on. Unless the pumps were changed, or the electrical was done in-house, I find it unlikely that the design is wrong.
There could be an issue with ultrasonic level indicators or float switches causing rapid cycling, and the 60 amp breaker would already be warm and possible trip when the other pump comes on.
I agree that we need more information from the original poster, such as do both pumps ever run at the same time, how many starts per hour, amperage readings, etcetera
They can be wrong.
We installed a small system similar to the OPs some years with the exception we had a fused SE disconnect ahead of the supplied controller. It was blowing the 60 amp fuses. I had the same question as OP. Why? I talked to the area Bussman fuse rep and we came up with the cycle time was too short. Telling that to the engineer that designed the whole thing was not met well. It took a few months but they changed the float levels. No problems since, other than the occasional 2x4 and underwear that don’t make it through.