You guys tease me to no end about my preaching the use of the megger for troubleshooting, so I thought I'd share a quick story from a service call this morning.
On Monday morning, I did a panel change out. I took out an old FPE panel, which featured several GFCI breakers, and replaced it with a Square D panel. My usual custom is to install GFCI receptacles at the point of use instead of installing new GFCI breakers, but due to the fact that this customer had "custom" receptacle covers, I just put in Square D GFCI breakers.
I did warn the customer after the panel swap that due to the fact that they had FPE equipment before, and their noted ability to not trip when they should, they may experience tripping now due to genuine reasons that are just now being realized by the new equipment. Sure enough, they call late yesterday that one of the GFCI breakers is tripping and won't reset. These calls can be quite time consuming to sort out.
First thing, when I arrived this morning at the customer's home, the homeowner starts ranting about the breaker being "bad". Since my troubleshooting would start with removal of the panel cover anyway, I did replace the breaker while the customer was watching for the main purpose of proving to the customer that the breaker isn't "bad". On showing that the new breaker trips too (I knew it would), he retired to the house proper for the rest of my time there.
I took the hot and neutral off the breaker, and took the ground wire for that circuit off the ground bar. I checked hot to ground and neutral to ground with my ohm meter, and got completely open readings with the ohm meter. I put a megger on it at 500 volts, and got a reading of less than 5 megohms from hot to ground and neutral to ground. I forget the exact number, but it's not important. What is important is that it showed up on the megger.
This circuit was labeled "garage and outdoor receptacles", which I knew was correct because I labeled it myself 2 days prior. I quickly unplugged all items from these locations and did the megger check with the same results.
Experience tells me that outdoor receptacles are more likely to trip GFCI's, so that's where I started. Took the front outdoor receptacle out, and redid the megger check right from that location. Same bad results. Put front receptacle back together, and moved on to the back outdoor receptacle. Took the back receptacle out, and repeated the megger check at that location. SUCCESS! Good results now. Put the megger on the formerly removed receptacle by itself, and it tested bad. The receptacle looked visually fine, save for the normal wear an old outdoor receptacle shows, but it tested bad with the megger. I suspect it had drawn damp and maybe had an insect nest inside of it. Installed a new rear receptacle, and put the wires back on the GFCI breaker, and now it resets and stays reset.
Moral of the story, how would you have found that as quickly without a megger? Trial and error, I suppose? Even if you'd have replaced that rear outdoor receptacle and found that the GFCI breaker would stay set up, there would be no way for you to provide any assured "clearance testing" that the entire problem is solved without a follow-up megger check. My total time in that house was less than an hour. For something that can be as cheap as 100 bucks, it sped up my troubleshooting process and gives me surety that the job is completely and permanently done.
On Monday morning, I did a panel change out. I took out an old FPE panel, which featured several GFCI breakers, and replaced it with a Square D panel. My usual custom is to install GFCI receptacles at the point of use instead of installing new GFCI breakers, but due to the fact that this customer had "custom" receptacle covers, I just put in Square D GFCI breakers.
I did warn the customer after the panel swap that due to the fact that they had FPE equipment before, and their noted ability to not trip when they should, they may experience tripping now due to genuine reasons that are just now being realized by the new equipment. Sure enough, they call late yesterday that one of the GFCI breakers is tripping and won't reset. These calls can be quite time consuming to sort out.
First thing, when I arrived this morning at the customer's home, the homeowner starts ranting about the breaker being "bad". Since my troubleshooting would start with removal of the panel cover anyway, I did replace the breaker while the customer was watching for the main purpose of proving to the customer that the breaker isn't "bad". On showing that the new breaker trips too (I knew it would), he retired to the house proper for the rest of my time there.
I took the hot and neutral off the breaker, and took the ground wire for that circuit off the ground bar. I checked hot to ground and neutral to ground with my ohm meter, and got completely open readings with the ohm meter. I put a megger on it at 500 volts, and got a reading of less than 5 megohms from hot to ground and neutral to ground. I forget the exact number, but it's not important. What is important is that it showed up on the megger.
This circuit was labeled "garage and outdoor receptacles", which I knew was correct because I labeled it myself 2 days prior. I quickly unplugged all items from these locations and did the megger check with the same results.
Experience tells me that outdoor receptacles are more likely to trip GFCI's, so that's where I started. Took the front outdoor receptacle out, and redid the megger check right from that location. Same bad results. Put front receptacle back together, and moved on to the back outdoor receptacle. Took the back receptacle out, and repeated the megger check at that location. SUCCESS! Good results now. Put the megger on the formerly removed receptacle by itself, and it tested bad. The receptacle looked visually fine, save for the normal wear an old outdoor receptacle shows, but it tested bad with the megger. I suspect it had drawn damp and maybe had an insect nest inside of it. Installed a new rear receptacle, and put the wires back on the GFCI breaker, and now it resets and stays reset.
Moral of the story, how would you have found that as quickly without a megger? Trial and error, I suppose? Even if you'd have replaced that rear outdoor receptacle and found that the GFCI breaker would stay set up, there would be no way for you to provide any assured "clearance testing" that the entire problem is solved without a follow-up megger check. My total time in that house was less than an hour. For something that can be as cheap as 100 bucks, it sped up my troubleshooting process and gives me surety that the job is completely and permanently done.