New golf carts service repair shop. The outlets circuits are all fed by GFCI breakers. there are 3 lighting circuits separate from the outlets and in separate conduit. Outlets mainly serve EZGO high frequency battery chargers. Before construction was totally complete the owner brought in some carts to charge. Came in the next morning turned on the lights and every GFCI breaker that had a charger plugged in tripped. Reset breakers and all worked fine. The breakers will trip only after the charger has been plugged in for a few minutes. If you turn on lights then plug in chargers they will not trip. We have been through all termination to clear up crossed neutrals or any other termination issues and all is checked out. Te Utility claims their stuff is OK also. Now, there is the old shop, on a separate service fed from the utility, same chargers, same lights and the only difference is the use of GFCI outlets. The only difference we can establish is the transformer is 60' from the old shop and 220' to the new shop and the utility has a reduced neutral feeding the meter ped. Has anyone ever encountered this before?