Wondering if any body has witnessed this? We have a golf cart repair shop. All of the outlets in the shop are protected by GFCI breakers (all single circuit separate nuetrals) All run in EMT. There are 3 lighting circuits, in their our raceway not shared with the outlet circuits. Building is wood frame steel siding and roof. There is a 200 amp service 1ph 120/240. Outlets are mainly used for charging golf carts, they use High frequency EZ-GO chargers. Here the thing when they come in the morning and turn on the lights it will trip every circuit breaker that has a charger plugged in to the outlet and plugged into the cart. But only the breakers on the same phase as the lighting. So if lighting circuit A phase is turned on the A phase outlets will trip, not the B phase outlets. We have have even tried to use a GFCI receptacle and get the same results. We have check every connection and went through every fixture to check for pinched wired, we have tried the hair dryer test to see if we had a ground neutral intertie and all test out. We are a little confused at this point because the shop 100 yards away, sme type of building, same fixtures same, panel except we used GFCI receptacles there instead of breakers and nothing trips in building