I have a customer with a 50 amp / 240 volt hot tub. The tub was tripping the breaker and the hot tub company replaced the motor. The tub would run for a few minutes, but then would trip.
It now trips as soon as the motor is turned on. After replacing the motor with the same results, he has replaced the circuit board as well. The breaker still trips. The lights will turn on without issue.
As the electrician, I looked at the tub after the other guy came to the end of what he knew to do. I have not done a thorough search, but the first thing I did was to disconnect the ground wire at the tub. The motor runs. At that time, I checked the voltage between the neutral and ground - 0 volts. As soon as the ground wire is connected, the motor trips.
The customer has had several electrical issues due to poor workmanship in the past that we have already remedied, so he asked us to replace the supply wire from the panel to the hot tub disconnect and to the tub. I told him replacing the incoming line to the breaker would not alleviate the problem because the breaker is detecting ground faults south of the breaker, not the incoming line, but we replaced it for his peace of mind.
The hot tub technician called tech support for the tub and they think there is an electrical issue within the house. Tech support recommended turning off all breakers to see if power was feeding back to ground.
My first question: If this were an issue, wouldn't it cause other ground faults to trip? (hot tub tech support says voltage going back to ground would not necessarily trip the ground fault receptacles, because they are different from the hot tub breaker - How so? ) By the way, with all breakers off, the hot tub still trips.
Second question: What is the best way to check the system for any "voltage leaks" if there are any? I am not getting any readings between neutral - ground.
Thank you for your input.
It now trips as soon as the motor is turned on. After replacing the motor with the same results, he has replaced the circuit board as well. The breaker still trips. The lights will turn on without issue.
As the electrician, I looked at the tub after the other guy came to the end of what he knew to do. I have not done a thorough search, but the first thing I did was to disconnect the ground wire at the tub. The motor runs. At that time, I checked the voltage between the neutral and ground - 0 volts. As soon as the ground wire is connected, the motor trips.
The customer has had several electrical issues due to poor workmanship in the past that we have already remedied, so he asked us to replace the supply wire from the panel to the hot tub disconnect and to the tub. I told him replacing the incoming line to the breaker would not alleviate the problem because the breaker is detecting ground faults south of the breaker, not the incoming line, but we replaced it for his peace of mind.
The hot tub technician called tech support for the tub and they think there is an electrical issue within the house. Tech support recommended turning off all breakers to see if power was feeding back to ground.
My first question: If this were an issue, wouldn't it cause other ground faults to trip? (hot tub tech support says voltage going back to ground would not necessarily trip the ground fault receptacles, because they are different from the hot tub breaker - How so? ) By the way, with all breakers off, the hot tub still trips.
Second question: What is the best way to check the system for any "voltage leaks" if there are any? I am not getting any readings between neutral - ground.
Thank you for your input.