I am performing a controlled plant power shutdown tomorrow on my system which is typically running at about 10MVA. To do this I am going to open our main 5kV Siemens GMI breaker rated for 3000A. This breaker feeds several 1500kVA transformers which will typically be in service during opening of the breaker.
My question is after we are done with the power outage what is the proper procedure for picking back up load with the main breaker. In other words when I go to rack my main breaker back in, can I have other various loads in the plant (transformers, etc...) connected or do I have to close the main breaker with no load connected at all? I guess what it boils down to, is what or where can I look at on the breaker to find out what load its rated to pick up.
In the past I've only been concerned that the inrush of the transformers all at once would trip the main, but is there anything elese to factor in here?
My question is after we are done with the power outage what is the proper procedure for picking back up load with the main breaker. In other words when I go to rack my main breaker back in, can I have other various loads in the plant (transformers, etc...) connected or do I have to close the main breaker with no load connected at all? I guess what it boils down to, is what or where can I look at on the breaker to find out what load its rated to pick up.