First...I started a thread back in August of 2013 named "Tripping Main"...this is an extension of that thread.
Lengthy post...bare with me.
I am in the process (took the winter off because, well, who plays baseball in the winter) of troubleshooting a 400 amp Main Breaker that tripped twice last summer. This breaker feeds a baseball field consisting of field lighting (1500 watt MH...approx 10 - 13 years old), a press box and concessions stand.
Service is 400 amp and with the lights on, there is a 246 - 250 amp load.
The lighting is split up into two 175 amp branch circuits feeding through a lighting contactor, each with a 122 amp load.
The concessions consists of a couple of refrigerators, freezers, cookers, microwaves, etc...certainly no more than a 50 amp load (note: test was done without concessions stand load).
We had a HOT & DRY summer last year...one of the days this breaker tripped had a 104 deg heat index...the other was cooler but I don't recall how much. The Panelboard is in direct sunlight in a N3R enclosure. I don't recall for sure, but I don't think it had rained with in many days previous of the tripping (we were in a drout so I doubt it).
Just last week (ambient temp of 33 deg), I borrowed (because I don't have $5k - $10k to buy one myself) a thermal scanner from our fire department and did an infrared scan (keep in mind I have no experience with infrared scanning). I turned the lights on and let them run for a little over an hour and scanned throughout that time period. I did not notice anything abnormal around the main breaker...both line and load connections were hot but both equally so and they only reached around 91 deg or so. I am keeping in mind the ambient temperature difference and wonder if the heat index would be a factor.
I hope this works (because I've had issues in the past and I'm not much of a tech geek) but here is my Evernote page with notes and pictures.
https://www.evernote.com/shard/s89/...12789336003f/72b1532bdf6b1316707683c03cda0b08
So...what ya'll think? Please ask for more info if needed and I will do my best to oblige.
Lengthy post...bare with me.
I am in the process (took the winter off because, well, who plays baseball in the winter) of troubleshooting a 400 amp Main Breaker that tripped twice last summer. This breaker feeds a baseball field consisting of field lighting (1500 watt MH...approx 10 - 13 years old), a press box and concessions stand.
Service is 400 amp and with the lights on, there is a 246 - 250 amp load.
The lighting is split up into two 175 amp branch circuits feeding through a lighting contactor, each with a 122 amp load.
The concessions consists of a couple of refrigerators, freezers, cookers, microwaves, etc...certainly no more than a 50 amp load (note: test was done without concessions stand load).
We had a HOT & DRY summer last year...one of the days this breaker tripped had a 104 deg heat index...the other was cooler but I don't recall how much. The Panelboard is in direct sunlight in a N3R enclosure. I don't recall for sure, but I don't think it had rained with in many days previous of the tripping (we were in a drout so I doubt it).
Just last week (ambient temp of 33 deg), I borrowed (because I don't have $5k - $10k to buy one myself) a thermal scanner from our fire department and did an infrared scan (keep in mind I have no experience with infrared scanning). I turned the lights on and let them run for a little over an hour and scanned throughout that time period. I did not notice anything abnormal around the main breaker...both line and load connections were hot but both equally so and they only reached around 91 deg or so. I am keeping in mind the ambient temperature difference and wonder if the heat index would be a factor.
I hope this works (because I've had issues in the past and I'm not much of a tech geek) but here is my Evernote page with notes and pictures.
https://www.evernote.com/shard/s89/...12789336003f/72b1532bdf6b1316707683c03cda0b08
So...what ya'll think? Please ask for more info if needed and I will do my best to oblige.