lazorko
Member
- Location
- Philadelphia
Today I got a call to troubleshoot an outdoor post light that hadn't been working for several weeks. The light has its own branch circuit, wired in UF. I verified a dead short on the 15A breaker, and opened the panel cover to disconnect the branch from the breaker for further troubleshooting - and noticed that the 100A main had tripped, too.
I thought that maybe I had hit the handle when removing the cover, and reset it.
After dissassembling and reassembling the post lamp I could find no apparent problems - oddly, the short had cleared and the lamp was operating normally. I assumed that maybe the last installer had left a few strands of wire loose from a wire nut that had caused an intermittant. I left the lamp on test for an hour (doing other work) before leaving.
Tonight, the HO called to say that her lights had gone out - the main breaker had tripped. The branch circuit breaker for the post lamp had also tripped. The meter and panel are back-to-back on the garage, and I suspect that the UF shares the trench with the underground POCO laterals on its way to the post light. Is there a possibility that there is some insulation damage allowing intermittant current to flow directly between the two sets? Or should I suspect bad coordination between the main breaker and the branch breaker (both Siemens)? Your insights are appreciated.
I thought that maybe I had hit the handle when removing the cover, and reset it.
After dissassembling and reassembling the post lamp I could find no apparent problems - oddly, the short had cleared and the lamp was operating normally. I assumed that maybe the last installer had left a few strands of wire loose from a wire nut that had caused an intermittant. I left the lamp on test for an hour (doing other work) before leaving.
Tonight, the HO called to say that her lights had gone out - the main breaker had tripped. The branch circuit breaker for the post lamp had also tripped. The meter and panel are back-to-back on the garage, and I suspect that the UF shares the trench with the underground POCO laterals on its way to the post light. Is there a possibility that there is some insulation damage allowing intermittant current to flow directly between the two sets? Or should I suspect bad coordination between the main breaker and the branch breaker (both Siemens)? Your insights are appreciated.