Working with a 10HP motor with reversing contactors that intermittently trips the MCC bucket. Not blowing any fuses or heaters dropping out starter, just trips the MCC circuit breaker.
Service: 460, 3-phase, 30-AMP with 150Amp instanteous trip in MCC bucket, goes to a 30-Amp fused disconnect near machine. #1 starter with proper heaters reside in MCC bucket. Reversing contactors are in the machine's electrical panel.
Motor: 460V, 3-phase, 10HP, Code G
Locked Motor Amps @ 80 Amps
Does not always happen on the starting of the motor. Double tapped one direction button once and had the breaker trip. The only thing I've seen similar to this is a short in a motor, here the breaker would trip in a intermittent fashion. Anyone have any other ideas?