Does anyone have a concern or see a problem with this?

Yes! There are typically a couple stages of worry. The first should be a low pressure warning light, the next stage is a auto trip on low pressure meaning you are getting to the point where the breaker can no longer safely interrupt current. Maaaybe you have a bad pressure switch but more likely you have a leak.
 

big john

Senior Member
Location
Portland, ME
Eh? You know that's a problem! What's the score?

Rare to see SF6 breakers without pressure gauges, I'd definitely double-check that against your density switch to see if maybe this was a control fault.
 

mbrooke

Batteries Included
Location
United States
Occupation
Technician
Yes! There are typically a couple stages of worry. The first should be a low pressure warning light, the next stage is a auto trip on low pressure meaning you are getting to the point where the breaker can no longer safely interrupt current. Maaaybe you have a bad pressure switch but more likely you have a leak.

These breakers that auto trip, are they configured that way standard from the manufacturer?

Eh? You know that's a problem! What's the score?

Rare to see SF6 breakers without pressure gauges, I'd definitely double-check that against your density switch to see if maybe this was a control fault.


Sorry for being vague. :ashamed1: Its being debated whether or not to trip breakers on low low rather than locking them out. The breakers in question are dead tank 15, 38, 123 and 362kv 3 phase breakers.
 