Does anyone have a concern or see a problem with this?
Does anyone have a concern or see a problem with this?
Yes! There are typically a couple stages of worry. The first should be a low pressure warning light, the next stage is a auto trip on low pressure meaning you are getting to the point where the breaker can no longer safely interrupt current. Maaaybe you have a bad pressure switch but more likely you have a leak.
Eh? You know that's a problem! What's the score?
Rare to see SF6 breakers without pressure gauges, I'd definitely double-check that against your density switch to see if maybe this was a control fault.
Does anyone have a concern or see a problem with this?