We are installing a powered rail system that is used for cranes and trolleys. I,m concerned about the way its designed, not sure how it should be wired and protected.
There is 480v three phase power run inside of a plastic rail, using flat copper bus, with a ground bus. A wheeled assembly runs inside the rail with three spring loaded connectors that ride aganst the surface of the flat bus, three per phase. Each connector has a # 10 wire that hooks to the same lug in a connection box.
I,m being told this is a parallel connection like those used in a switchgear feed,
that each wire handles 1/3 the load and rated for 30 amps with a 90 amp total rating.
The feed to the rail is 125 amps. Wire is 1/0 from breaker to rail connection box.
The powered assembly will connect to a timber tote used at a sawmill, running hydraulic motors, and transformed also for control power.
It is a ul listed system.
Questions:
Is it a true parallel connection?
How do I protect the #10 wires correctly?
What else do I need to do to make this a correct installation?
Thanks
Kurt
There is 480v three phase power run inside of a plastic rail, using flat copper bus, with a ground bus. A wheeled assembly runs inside the rail with three spring loaded connectors that ride aganst the surface of the flat bus, three per phase. Each connector has a # 10 wire that hooks to the same lug in a connection box.
I,m being told this is a parallel connection like those used in a switchgear feed,
that each wire handles 1/3 the load and rated for 30 amps with a 90 amp total rating.
The feed to the rail is 125 amps. Wire is 1/0 from breaker to rail connection box.
The powered assembly will connect to a timber tote used at a sawmill, running hydraulic motors, and transformed also for control power.
It is a ul listed system.
Questions:
Is it a true parallel connection?
How do I protect the #10 wires correctly?
What else do I need to do to make this a correct installation?
Thanks
Kurt