nickelec

Senior Member
Location
US
Here are some pics
0df26de0016c52cf73824a58b3f231a6.jpg
29af53bf100e66a0d93def7219f7a555.jpg


Sent from my SM-G935P using Tapatalk
 

Chamuit

Grumpy Old Man
Location
Texas
Occupation
Electrician
Sounds like the neutral wire was lifted somewhere and tied into the hots. That would give you 120 V on the neutral conductor and the underground conductor. As long as that was not shorted out somewhere or you wouldn't blow any breakers or fuses.
 

markebenson

Senior Member
Location
fl
I find there is no value in repairing these kind of things with very old existing wiring. You can sooner run a new wire than troubleshoot & repair old unsafe wiring.
 

kwired

Electron manager
Location
NE Nebraska
I find there is no value in repairing these kind of things with very old existing wiring. You can sooner run a new wire than troubleshoot & repair old unsafe wiring.
I would assume you would at least look at some of the more obvious places where a loose connection may exist before defaulting to "replace everything" Some old wiring is in safer condition then some improperly installed new wiring BTW.
 